How to replace BCU06-ETH by PM90-ETH?
We have a bottle blowing machine having 24 blowing mould.In this machine 7 ABB pls are used. Six BCU06 are used for controlling of 24 moulds. Each BCU06 control 4 no of moulds.A PM582 is used as a host.Now we want to replace a BCU06-ETH with PM590-ETH using CodeSys V2.3.
I have the machine program.
Please let me know the replacement procedure.
A picture of the communication system is attached for your understanding.
Regards,
Kaisar
I have the machine program.
Please let me know the replacement procedure.
A picture of the communication system is attached for your understanding.
Regards,
Kaisar

Voted best answer
a BCU06 is a V2 Codesys PLC. I recommend to transfer the PLC-program with export/import from Codesys. I believe there is no mechanism to transfer the configuration in any automated way, because it is a Pre-ControlBuilder project. You need to create a new Automation-Builder Project and edit the configuration manually, then export the Codesys program and import it into the new project.