Customer got flood of alarms 'S_Status' Input Record quality: Bad. Customer has Hart devices. See Snapshots
Answers
Alarm Expressions supervises their input properties and raises alarms on bad input quality.
Check the OPC server feeding the expressions. Likely it send a shower of bad quality - maybe it even restarted?
These alarms can be suppressed by modifying a General Property, see the user's guide.
Check the OPC server feeding the expressions. Likely it send a shower of bad quality - maybe it even restarted?
These alarms can be suppressed by modifying a General Property, see the user's guide.
by Rick Myers SSG5 Rank: 152 on 3/1/2020 3:37:33 PM | Like (0) | Report
All the events are not listed in the alarm list anymore the customer cleared the alarms. The alarms came into the event list appeared to be RTN. Need to review the alarm details. Will use the History Event list to look at the alarm details
by elemravi Rank: 33 on 3/1/2020 8:30:55 PM | Like (0) | Report
Probably a bad OPC data source definition or bad OPC service. What is the quality of S_STATUS in Property Translation Extended aspect on the hardware unit?
Is there any system status asset monitor configured on the Hardware units?