ABB Drive to trigger the fault for testing the relay Fault output.
For Drive like ACS150,ACS355 and ACS580 any easiest way to trigger the fault? Require to testing for fault indication light. Another question is for overcurent or overvoltage how to trigger it when presentation, any setting need to set?
Answers
Greetings,
As a Fault Trigger easiest way is to use Panel Lost but AFAIK ACS150 does not have that kind of fault.
So you can use AI<Min under parameter 30.01 as fault trigger. By the way you need to use AI1 as reference input.
Hope it helps.
As a Fault Trigger easiest way is to use Panel Lost but AFAIK ACS150 does not have that kind of fault.
So you can use AI<Min under parameter 30.01 as fault trigger. By the way you need to use AI1 as reference input.
Hope it helps.
Hi
in addition to Titus answer, you can use for example the output relay (parameter 14.01 in ACS355) to set the action of the relay as generic fault.
The same function could be activate by the parameter 18.05 always in ACS355, for the digital output (transistor).
In the FW manual (in all series of ABB drives) you can find some instruction to define the action of the output, to activate for specific fault or alarm or by generic fault
Hope this help you
BR
Flavio
in addition to Titus answer, you can use for example the output relay (parameter 14.01 in ACS355) to set the action of the relay as generic fault.
The same function could be activate by the parameter 18.05 always in ACS355, for the digital output (transistor).
In the FW manual (in all series of ABB drives) you can find some instruction to define the action of the output, to activate for specific fault or alarm or by generic fault
Hope this help you
BR
Flavio
Source: FW MANUAL ABB DRIVES
Add new comment