Hi,
I have 23 controllers and i work with minerals library. The problem is in the command "acknowledge all visible alarms" that recognize every alarm less the signals ( AIC, AIS, DIS, DIC, MOT, etc) in 02 controllers in specific in the same workplace.
In this signals not recognized you can enter to the faceplate and recognize the alarm.
Thank you,
I have 23 controllers and i work with minerals library. The problem is in the command "acknowledge all visible alarms" that recognize every alarm less the signals ( AIC, AIS, DIS, DIC, MOT, etc) in 02 controllers in specific in the same workplace.
In this signals not recognized you can enter to the faceplate and recognize the alarm.
Thank you,
Answers
The Acknowledge all visible alarms function require that the user has Operate permission on all affected objects.
Try acknowledge all from an admin account, if it can acknowledge all you know there is one or more objects the regular user does not have permission on.
Try acknowledge all from an admin account, if it can acknowledge all you know there is one or more objects the regular user does not have permission on.
by backdraft
I understand you can acknowledge from Faceplate, but can you as well acknowledge from alarm list for those alarms - do you have an Alarm Band shown in Workplace for those Alarms and do the number active/unack Alarms match?