Control Builder Error 9118 - 800xA Version 5.1
I have imported on 800xA the GSXML file for a Siemens Simocode PROV N, in order to read the information from the simocode device via profinet using the PM891 ptofinet board CI871.
I have created the variables (BoolIO and DintIO) and connected on the hardware.
The BoolIO variable are ok. When I try to connect the DintIO variable on the hardware channel and compile I receive the error:
“Error 9118: PM781_E2:HW Connections: Variable connections in conflict ….”
The DintIO variable are non used on other hardware channel.
Some one know the reason for this type of error ?
Best regards
Angelo.
Answers
Hi,
ABB IO Cards (S800/S900) will support only BoolIO and RealIO. If you want to use DintIO then you should use the conversion block and need to connect to hardware IO channel.
ABB IO Cards (S800/S900) will support only BoolIO and RealIO. If you want to use DintIO then you should use the conversion block and need to connect to hardware IO channel.