Reset fault of ABB ACS580
Hi
I want to reset faults of ABB ACS580 drive by set parameter.
How can i do that?
Thanks.
Voted best answer
Hi
Or you can simply click the left side up of the CDP(display) ,and you can the see the option of fault ,if there is any fault you can reset as simple.
Or you can simply click the left side up of the CDP(display) ,and you can the see the option of fault ,if there is any fault you can reset as simple.
Answers
Hi
you can use parameter 96.51 to reset fault and event logger
BR
Flavio
you can use parameter 96.51 to reset fault and event logger
BR
Flavio
Source: ACS580 FW MANUAL