Alarms & trends from 800xA to Smart Client
Hi All.
Can someone please help me out on how to configure the trends for smart client that can be seen in 800xA.
can we upload the same trend template as in 800xA to smart client ?
I am using xA 6.0.3.2
Can someone please help me out on how to configure the trends for smart client that can be seen in 800xA.
can we upload the same trend template as in 800xA to smart client ?
I am using xA 6.0.3.2
Voted best answer
Trend Displays configured in 800xA can be imported into Smart Client Panels for display purposes. I have attached a short description of how this and PG2 Graphics can be imported into Smart Client Panels. Please note that for 800xA Trend Displays, that when they are imported, the static portion of the display/panel is changed to exhibit the structure of a Smart Client native Trend Panel, however, the actual Tags and associated information are the same as in 800xA. As a reminder, both the PG2 Graphics and Trend Displays from 800xA will only be available with proper licensing and with the proper installation of ALL the prerequisites for the Smart Client product. One final comment, you mentioned that you wanted to have Smart Client Trends to be seen in 800xA, (I assume you mean the OWP). Trend Panels configured in the Native Smart Client Trend configuration cannot be imported back into the 800xA system for display in an OWP. It also needs to be noted that when importing the PG2 & Trend displays from 800xA into Smart Client, that these cannot be modified with the Smart Client native tools.
Regards,
Geof Ledin
Regards,
Geof Ledin
Add new comment