multiple soft controllers - mms communications between controllers not working
In 800xA SV5.1 is it possible to have communication between soft controllers?
I have started two soft controllers. After downloading to both controllers the Communication Variable status has a timeout
In the Diagnostics Overview the transaction count is incrementing but variables/s is 0
I have started two soft controllers. After downloading to both controllers the Communication Variable status has a timeout
In the Diagnostics Overview the transaction count is incrementing but variables/s is 0
Answers
Make sure you specify the Port.
Default is :2 , if you run more than 1 in a node, use :3, :4 etc as defined in your soft controller start up definitions.
Default is :2 , if you run more than 1 in a node, use :3, :4 etc as defined in your soft controller start up definitions.
The problem appears to be with the version of soft controller - using 5.1.0/1 (Build 5.1.100.13)
(Work around is to have multiple VM's running one SC in each)
(Work around is to have multiple VM's running one SC in each)