AC450 Database Error
Hello, all.
In an AC450 CPU (SWQC07-BAS41*4.0 ) I've created an AI810 IO Card using the command CRDB.
I can open all the channels except the last one. When i try to open it i get a database population error (see the atached files).
Regards
In an AC450 CPU (SWQC07-BAS41*4.0 ) I've created an AI810 IO Card using the command CRDB.
I can open all the channels except the last one. When i try to open it i get a database population error (see the atached files).
Regards
Answers
I go the same error message but it happened with me when I try set IMPL=1 or 0 for the CI522 (Database AF100_1) Or CI820 (Database AF100IOS_1 for example) and I don't know the reason but it works properly when I put the controller in Configuration Mode (Econfig).
I also have the same software version.
I also have the same software version.
Hello
Have you tried with system command FINS 6,XX where XX is the logical record for resp channel ?
6 is Logical file for AI and the channel Logical records are in consecutive order from 1 th the last channel.
Do all records exist for the AI810 board ?
MVH Jan-Erik
Have you tried with system command FINS 6,XX where XX is the logical record for resp channel ?
6 is Logical file for AI and the channel Logical records are in consecutive order from 1 th the last channel.
Do all records exist for the AI810 board ?
MVH Jan-Erik
Perhaps you have exceeded your allocation of AI Signals? Check with DIMDB to see your allowed count of AI's (call this number #) and then use MDB 6.# to see if it already exists. You may find that 6.# is channel 7 on your AI810 and thus channel 8 could not be created.