Where is SMV measurement for REF615?
Hi,
I am still struggling with the Sample Value subscription on the ABB REF 615 IED. I am sending some voltage values via Sample Values with a simulator to the IED. When I use Wireshark to monitor the switch to which the IED is connected, I can see the values as SV packets. However, I do not see the values anywhere in PCM600, the IED's WHMI or LHMI. The measurement section in WHMI just shows 0 for all values.
Where are the measurements located? Where can I check in PCM600 and see the values which are being sent to the IED?
I have tried contacting ABB support but they are unresponsive and this is making me a bit frustrated. So, if you can let me know which section of PCM600 should I check to see the values, I'd appreciate it.
Also, should I do any configuration on Signal Matrix for the SV subscription? From what I understand, I can only connect SMRECV to a TVTR and that is it.
I have shared pictures of my configuration. Any help is appreciated. Thanks!
Answers
You can find the details how to configure SMV Receiving from the 615 series IEC 61850 Engineering Guide, Chapter 6.3:
https://search.abb.com/library/Downlo...
You don't need to do any configuration in Signal Matrix.
After you have configured the SMV Receiving on the Application Configuration (Chapter 6.4 in the Guide) and everything is working, you will start to see the 9-2 measurements in the relay's normal measurement view. So the SMV voltages replaces the local measurements.
Chapter 6.5 of the IEC 61850 Engineering Guide gives some advices how to verify that the configuration is done properly.
I hope this helps to get forward.