SOE Alarm are not generating from DI830 Card ( 800XA 6.0.3.2)
We have 800xa system with DI830 card used to create the SOE alarm for Digital Inputs.
We have created the alarm block and passed the SinglaID and SOE alarm is enabled in card level ,we are not getting alarm in the system ?
We have created the alarm block and passed the SinglaID and SOE alarm is enabled in card level ,we are not getting alarm in the system ?
Answers
Hi,
First of all, DI830 can send SOE timestamp through ModuleBus only. Hopefully this is your configuration?
Which FB do you use as SOE receiver for Alarming?
From my experience PP Lib 6.1 DIS does not work for SOE.
AlarmCond FB works fine.
Check also CPU log whether you see there any SOE warnings?
Use SignalID from CPU log warning for right channel addressing at AlarmCond input.
First of all, DI830 can send SOE timestamp through ModuleBus only. Hopefully this is your configuration?
Which FB do you use as SOE receiver for Alarming?
From my experience PP Lib 6.1 DIS does not work for SOE.
AlarmCond FB works fine.
Check also CPU log whether you see there any SOE warnings?
Use SignalID from CPU log warning for right channel addressing at AlarmCond input.