Siemens ET200 I/O - AC800M Profinet
Hi!
Is it possible to connect Siemens ET200 I/O via Profinet to a AC800M CI871? And if so what files etc do I need?
Is it possible to connect Siemens ET200 I/O via Profinet to a AC800M CI871? And if so what files etc do I need?
Answers
You required GSDML file for communication between Siemens & ABB system through Profinet
Is there a Device Integration Center for Profinet like the one for Profibus?
Is it possible to find a tested GSDML file for ET200SP that works with 800xA 6.1?
Is it possible to find a tested GSDML file for ET200SP that works with 800xA 6.1?
I have connected ET200SP motorstarters (DS) to Profinet.
Had to modify GSDML file to be able to import to ABB. Supportdesk helped with an initial version of the modified file.
Attach the file here.
Had to modify GSDML file to be able to import to ABB. Supportdesk helped with an initial version of the modified file.
Attach the file here.
by Asp Rank: 149 on 1/21/2020 6:41:54 AM | Like (0) | Report
The Siemens I/O i ET200SP