Error in Quality in the system 800xA Bad/Configuration Error
Hello,
I have problem with some tags into the system 800xA, some time, anysome tags no connect with the OPC (Rslinx), but other tags yes. Then so this variables will connect, I go to "Signal Configuration", after that click in Not Connected, and I do Deployed. And I so connected, the problem happens when the Server (PC) so resert or lost comunnication
You help me with this problem?
Thanks
I have problem with some tags into the system 800xA, some time, anysome tags no connect with the OPC (Rslinx), but other tags yes. Then so this variables will connect, I go to "Signal Configuration", after that click in Not Connected, and I do Deployed. And I so connected, the problem happens when the Server (PC) so resert or lost comunnication
You help me with this problem?
Thanks
Voted best answer
Hi!
I guess a restart of the "PLC Softpoint Service" (Service Structure), might solve problems with loss of connection to "external" OPC properties like "Value".
All the other properties reside "inside" the object model of 800xA PLC Connect (ie "internal" properties), and still will be "Good" if the connection to OPC is broken.
BR
I guess a restart of the "PLC Softpoint Service" (Service Structure), might solve problems with loss of connection to "external" OPC properties like "Value".
All the other properties reside "inside" the object model of 800xA PLC Connect (ie "internal" properties), and still will be "Good" if the connection to OPC is broken.
BR
Answers
There is no use to spam AKS with same questions again and again.
I have very little knowledge in PLC Connect and its OPC drivers; RsLinx - I would have answered to your previous post if I had anything to contribute with.
If you want support from ABB; please contact your regional ABB support center. Colombia belongs to the US L3 center based in Cleveland, OH, USA. Try this email: us-iapcp-l3-supportline@abb.com
I have very little knowledge in PLC Connect and its OPC drivers; RsLinx - I would have answered to your previous post if I had anything to contribute with.
If you want support from ABB; please contact your regional ABB support center. Colombia belongs to the US L3 center based in Cleveland, OH, USA. Try this email: us-iapcp-l3-supportline@abb.com
Give suitable rights in the properties of the resepctive service so that we PC will get restarted this will reconnect.