How to solve ACS800 ( 4110 ) fault ?
Dear Mr / stefan
I face a problem with Abb drive ACS 800 give me fault with code ( 4110 ) control board temp ... How to solve this problem ... Change RMIO module or what ???
FYI ... the drive temp and RMIO module temps are very cold
I face a problem with Abb drive ACS 800 give me fault with code ( 4110 ) control board temp ... How to solve this problem ... Change RMIO module or what ???
FYI ... the drive temp and RMIO module temps are very cold
Answers
Hi
the error signal 4110 - control board temperature alarm - can originate from a failure of the sensors that are used for the measurement, rather than a real over temperature of the board. I recommend replacing the control board but if you are not adequately prepared, have it done by the ABB Service in your area.
BR
Flavio
the error signal 4110 - control board temperature alarm - can originate from a failure of the sensors that are used for the measurement, rather than a real over temperature of the board. I recommend replacing the control board but if you are not adequately prepared, have it done by the ABB Service in your area.
BR
Flavio