Sir,
We are having one Installed PLC which we are using since last 10 year. 07 KT 97E
There is ONE HMI also. We want to communicate with PLC to set some parameter.
Please let me know software and its target file. If Software is COdesys then which version is required to communicate.
How I can get the required target file for the same
Regards
Mayank
+919997998314Answers
Hi,
I have been working with that AC31 PLC many years ago. That time I used software 907 AC1131 .
You need also backup of PLC project.
I have been working with that AC31 PLC many years ago. That time I used software 907 AC1131 .
You need also backup of PLC project.
Hi
as Kamil rightly reminded you, the SW Codesys and more generally the Automation Builder platform, are used on ABB's new AC500 series PLCs and accessories, such as HMIs.
For the old 07 KT 97 series, I suggest you to contact the nearest ABB distributor and get help from the ABB commercial / service organization that will be able to provide you with the necessary support.
BR
Flavio
as Kamil rightly reminded you, the SW Codesys and more generally the Automation Builder platform, are used on ABB's new AC500 series PLCs and accessories, such as HMIs.
For the old 07 KT 97 series, I suggest you to contact the nearest ABB distributor and get help from the ABB commercial / service organization that will be able to provide you with the necessary support.
BR
Flavio
There are several versions of the software 907AC1131 which is used to program series 40, 50 and 90 controllers eq. 07KT97. At least versions 4.x were based on Codesys 2.1 and versions 5.x Codesys 2.3.