What is the use of internal CF card in PP865A. Does it come along with the panel. PP865A gone blank after some day
I downloaded a project to a PP865A which worked but after 2-3 weeks it didnt even switch on and on performing a self test it showed internal cf card failure.
What should i do now sir? Any suggestions u could give me
(firmware: v4 and software: panel builder 800 v5.0)
Answers
Usually, you don't need additional internal or external CF card, the project will be saved in panel's memory. It have enough memory for a quite big project.
Un-install internal CF card, go to the Terminal Options and select Internal size (MB) = 0. Do transfer of the project.
My experience is that you can have a troubles, in case of using not supported CF cards - look below
Press F1 with open Terminal options and read the help.
From the manuals:
"An internal Compact Flash memory card can be used to expand the project memory
When using an internal Compact Flash memory card, no external Compact Flash memory card can be used. An external USB Flash drive can be used for the same functions as an external Compact Flash card.
Compact Flash cards of type I and II are supported by the operator panels. Recommended Compact Flash memory cards are SiliconSystems SiliconDrive, SanDisk Industrial Grade and Cactus 203-, 302-, 303-series.
The size of the internal memory card must be entered in the configuration tool for the operator panel
1. Select Setup/Terminal Options
3. Enter the size of the internal memory card under Memory card settings/Internal"
Source: 3BSE043448R401
/What-is-the-use-of-internal-CF-card-in-PP865A-Does-it-come-along-with-the-pane
l-PP865A-gone-blank-after-some-day
by arunvt1992 Rank: 666 on 12/14/2019 6:56:18 PM | Like (0) | Report
There is not amount of information given in the help menu of the software or the manuals.
Add new comment