Confirm Operation window appears in multiple Workstation at same time for same operation
I have configured the Bool values for Pushbuttons used in HMI operations for SIL3 project and system version is 6.0.3-2 . when i keep same graphics window in two or more operating or Engineering stations at the same time and click push button in one system ,a confirm operation window appears in that worksation and also appears in other worksations where i have kept the same graphics window too ..it is confusing the operator .kindly advise what i have change in configuration..this is not happening for valves or motor faceplate operation confirmation. I have configured the Confirm and access enable for bool values in SIL access .
kindly advice..thanks in advance
kindly advice..thanks in advance
Answers
I believe the Safe Online Write to SIL application expects the input to be made from a faceplate where the object locking mechanism prevents more than one operator to have simultaneous access to the one and same object.
You should contact your regional ABB support center and ask for official support.
Add new comment