PM 866 controller communication issue
Firstly we have installed PM864 AK 02 ABB (32 mb)make controller ,after 4 years ins given problem .controller lost his communication with DCS .on desktop all values are cross but controller working properly he controlled all units properly but his memory is used 85%.as per ABB recommendation we have fitted PM866 AK 02 ( 64 mb) controller but after 7 days we are facing same above problem so tell us how to solved this problum
Answers
The log indicate problems with the networking, or networking hardware.
However, the below drew my attention
I 2019-12-01 19:18:57.092 Network Interface 172.16.4.151 (255.255.252.0 ) : 00-00-23-0d-9e-54
I 2019-12-01 19:18:57.097 Network Interface 172.17.4.151 (255.255.252.0 ) : 00-00-23-0d-9e-55
I 2019-12-01 19:18:57.102 Backup Interface 172.16.6.151 (255.255.252.0 ) (default rule)
I 2019-12-01 19:18:57.103 Backup Interface 172.17.4.151 (255.255.252.0 ) (explicit set)
The backup controller's secondary Ethernet interface setting is wrong; instead of using default rule (which adds 0.0.2.0 to the primary controller's counterpart) it has been manually set to the same address as the primary controller's secondary address. A manual setting is OK, but must be routable and not make conflict with any other address.
Please correct this conflict (serial cable, IPConfig.exe, controller reset, set Backup Interface --> Secondary --> Use Default Rule).
Then please download the application to the controller again and check the controller log once more.
by shmo Rank: 581 on 12/4/2019 2:01:42 AM | Like (0) | Report
if you have changed the controller & still facing communication issues then probably the communication interafece is the issue.
Have you tried changing the ports used on the network switch? any damage on ethernet cable connecting the controller to the networ switch, etc?
by suresh_jagatap Rank: 4775 on 12/4/2019 2:07:44 AM | Like (0) | Report
after changing controller its working 7 days. after 7 days its memory is 80% full and communication fail with desktop. all values are crossed
by shmo Rank: 581 on 12/4/2019 2:14:43 AM | Like (0) | Report
hmmmmm ... ABB controllers cut external communication on high loads, to take care of their local control duties. That explains why your controller is working properly toward the equipment (control duties). However I think this usually happens at 95+% ...
You can check if any extensive logging has been enabled recently? Something that was done on PM864 and now also followed on PM866, as I assumed you set it up with same settings ? Sounds like an accumulative thing that gives a memory flaw after a while ...
by ATP
Attach controller logs
by suresh_jagatap Rank: 4775 on 12/4/2019 3:56:10 AM | Like (0) | Report
I 1980-01-01 00:00:00.000 Executable is: C:\Program Files (x86)\ABB Industrial IT\Control IT\OPC Server for AC 800M 5.1\Bin\AC800MC_OpcServer.exe
I 1980-01-01 00:00:00.000 OPC server is registered as NT service.
I 1980-01-01 00:00:00.000 User: 800xAService
Operating System Information
============================
Caption: Microsoft Windows 7 Professional
CSDVersion: Service Pack 1
Version: 6.1.7601
OSLanguage: 1033
ForegroundApplicationBoost: 2
LastBootUpTime: 20191123122606.110000+330
Computer System Information
===========================
Caption: ES1
Domain: WORKGROUP
Manufacturer: Dell Inc.
Model: Precision Tower 3620
Name: ES1
NumberOfProcessors: 1
SystemType: x64-based PC
Processor Information
=====================
DeviceID: CPU0
Caption: Intel64 Family 6 Model 94 Stepping 3
Manufacturer: GenuineIntel
Name: Intel(R) Xeon(R) CPU E3-1220 v5 @ 3.00GHz
CurrentClockSpeed: 3001
NumberOfCores: 4
NumberOfLogicalProcessors: 4
I 1980-01-01 00:00:00.000 OPC server started as NT service.
I 1980-01-01 00:00:00.000 Starting MMS Server
I 1980-01-01 00:00:00.000 MMS Server running
I 1980-01-01 00:00:00.000 MMS Server connected
I 1980-01-01 00:00:00.000
I 1980-01-01 00:00:00.000 Product : OPC Server for AC 800M
I 1980-01-01 00:00:00.000 Version : 5.1.0/1 (Build 5.1.100.13)
I 1980-01-01 00:00:00.000 Created : 2011-04-16
I 1980-01-01 00:00:00.000 ABB AB
I 1980-01-01 00:00:00.000
I 1980-01-01 00:00:00.000 Working folder: C:\ABB Industrial IT Data\Control IT Data\OPC Server for AC 800M\
I 1980-01-01 00:00:00.000 Using C heap
I 1980-01-01 00:00:00.000 CodePage: 1252, Character set: ANSI - Western/Latin I
I 1980-01-01 00:00:00.000 Timer resolution 1 millisecond
I 1980-01-01 00:00:00.000 Reading systemsetup.sys.
I 1980-01-01 00:00:00.000 Priority raised to above normal.
I 1980-01-01 00:00:00.000 MMS Server is running
I 1980-01-01 00:00:00.000 Network address is 172.17.4.11:22, 172.16.4.11:22.
I 2019-11-23 12:26:32.530 OPC server started.
I 2019-11-23 12:26:32.530 Autoloading configuration...
I 2019-11-23 12:26:33.411 OPC Data Access: Connected to controller: I 2019-11-23 12:26:33.411 172.16.4.151
I 2019-11-23 12:26:33.478 Autoload configuration finished.
I 2019-11-23 12:26:54.913 OPCAE - Start of subscription. OPC client Id = 0 . SaveSub not enabled.
I 2019-11-23 12:26:54.988 OPCAE - Start of subscription. OPC client Id = 0 . SaveSub not enabled.
E 2019-12-01 18:31:41.269 Error when calling GetCapabilityListReq
I 2019-12-01 18:31:41.269 AssocNotExisting
E 2019-12-01 18:32:02.553 On Unit= SubDataAccess 172.16.4.151 ConnErr OPCServer 5500 Conn error to DA subscr controller
I 2019-12-01 19:18:32.914 OPC Data Access: Contact again with controller: I 2019-12-01 19:18:32.914 172.16.4.151
E 2019-12-01 19:18:32.914 Off Unit= SubDataAccess 172.16.4.151 ConnErr OPCServer 5500 Conn error to DA subscr controller
E 2019-12-01 19:18:50.649 On Unit= SubAlarmEvent 172.16.4.151 ConnErr OPCServer 6500 Conn error to AE subscr controller
E 2019-12-01 19:18:54.082 On Unit= SubDataAccess 172.16.4.151 ConnErr OPCServer 5500 Conn error to DA subscr controller
E 2019-12-01 19:19:32.601 Off Unit= SubAlarmEvent 172.16.4.151 ConnErr OPCServer 6500 Conn error to AE subscr controller
W 2019-12-01 19:19:32.609 Unit= _SWAlarmEvent OPCServer 6002 Failed to subscribe on 172.16.4.151
I 2019-12-01 19:19:32.897 OPC Data Access: Contact again with controller: I 2019-12-01 19:19:32.897 172.16.4.151
E 2019-12-01 19:19:32.897 Off Unit= SubDataAccess 172.16.4.151 ConnErr OPCServer 5500 Conn error to DA subscr controller
E 2019-12-01 19:19:38.893 All Items have a Quality that is NOT GOOD. Setting status as Not Configured.
I 2019-12-01 19:21:36.237 OPCAE - Start of subscription. OPC client Id = 0 . SaveSub not enabled.
I 2019-12-01 19:21:36.253 OPCAE - Start of subscription. OPC client Id = 0 . SaveSub not enabled.
I 2019-12-01 19:26:22.622 OPCAE - End of subscription. OPC client Id = 0 . SaveSub not enabled.
I 2019-12-01 19:26:22.624 OPCAE - End of subscription. OPC client Id = 0 . SaveSub not enabled.
by ATP
Attach the controller log, The attached one is OPC logs. To take the log of the controller, go to the particular controller in Control builder, right click--> remote system -->Show Controller log,
by suresh_jagatap Rank: 4775 on 12/4/2019 5:07:38 AM | Like (0) | Report
##########################
=== Latest startup-log ===
##########################
es (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 40 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask): memPartAlloc: block too big 40 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask): memPartAlloc: block too big 40 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask): memPartAlloc: block too big 40 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 40 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
W 2019-12-01 19:17:47.020 Unit= _SWFirmware Controller_1 1012 Undecl ext event 0.11.106.5 false
W 2019-12-01 19:17:47.024 Unit= _SWFirmware Controller_1 1012 Undecl ext event 0.11.106.6 true
W 2019-12-01 19:17:47.025 Unit= _SWFirmware Controller_1 1012 Undecl ext event 0.11.106.6 false
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 40 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 40 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
W 2019-12-01 19:17:53.256 A/E Burst: Prevented 16 alarms & events from being printed in the log, refer to an OPC AE client for more info.
W 2019-12-01 19:17:48.857 Unit= _SWFirmware Controller_1 1012 Undecl ext event 0.11.101.10 true
W 2019-12-01 19:17:49.025 Unit= _SWFirmware Controller_1 1012 Undecl ext event 0.11.101.10 false
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
W 2019-12-01 19:17:48.380 Unit= _SWFirmware Controller_1 1012 Undecl ext event 0.11.106.16 true
W 2019-12-01 19:17:48.417 Unit= _SWFirmware Controller_1 1012 Undecl ext event 0.11.106.15 true
W 2019-12-01 19:17:48.425 Unit= _SWFirmware Controller_1 1012 Undecl ext event 0.11.106.16 false
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
W 2019-12-01 19:17:48.284 Unit= _SWFirmware Controller_1 1012 Undecl ext event 0.11.103.9 false
W 2019-12-01 19:17:48.309 Unit= _SWFirmware Controller_1 1012 Undecl ext event 0.11.103.9 true
W 2019-12-01 19:17:48.402 Unit= _SWFirmware Controller_1 1012 Undecl ext event 0.11.103.9 false
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 40 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 18 bytes (0x8 aligned) in partition 0x453c98
0xc5e798 (tNetTask):
arp: (null) is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask): memPartAlloc: block too big 40 bytes (0x8 aligned) in partition 0x453c98
W 2019-12-01 19:18:00.558 A/E Burst: Prevented 16 alarms & events from being printed in the log, refer to an OPC AE client for more info.
W 2019-12-01 19:17:48.875 Unit= _SWFirmware Controller_1 1012 Undecl ext event 0.11.103.8 false
W 2019-12-01 19:17:58.672 Unit= _SWFirmware Controller_1 1012 Undecl ext event 0.11.103.9 false
E 2019-12-01 19:18:01.306 ErrorHandler PM: 4087 The Shared Heap is out of memory (2,2)
E 2019-12-01 19:18:01.306 Create heap element failed, Size: 157, EType: 19, Kind: 2!
W 2019-12-01 19:18:01.307 WARNING: Out of memory!
Heap full!
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.13 is on cpm0 but got reply from a4:1f:72:84:33:76 on cpm1
This PM has been automatically restarted.
Reason:
- INIT_SWITCH, INIT-SWITCH pressed
_____________________________________________________________________________
0
No Firmware Upgraded
5.5.2 2096
Watchdog is enabled with timeout = 1986 us
This is Lower CPU running as Primary CPU.
aching interface lo0...done
TCPIP CONFIG
I 1979-12-31 00:00:00.000 Printer thread MMS-plugin, streaming disabled
I 1979-12-31 00:00:00.000 Printer thread, Filter: Disabled, Mode: Classic, BUM: Disabled
I 1979-12-31 00:00:00.000 Low memory (0x00-0x3F) access detection initiated
I 1979-12-31 00:00:00.000 Built: Apr 16 2011 20:45:48
I 2019-12-01 19:18:56.565 Autorestart is disabled
I 2019-12-01 19:18:56.565 Initialized at: 19:18:56 2019-12-01 (local time)
I 2019-12-01 19:18:56.565 System time quality: GOOD
I 2019-12-01 19:18:56.566 Current time zone: India Standard Time
I 2019-12-01 19:18:56.566 It took 0.432 ms to conclude previous system shutdown
I 2019-12-01 19:18:56.567 CPU-core running at 133 Mc, bus /2, to=16.0 us
I 2019-12-01 19:18:57.086
I 2019-12-01 19:18:57.092 Network Interface 172.16.4.151 (255.255.252.0 ) : 00-00-23-0d-9e-54
I 2019-12-01 19:18:57.097 Network Interface 172.17.4.151 (255.255.252.0 ) : 00-00-23-0d-9e-55
I 2019-12-01 19:18:57.102 Backup Interface 172.16.6.151 (255.255.252.0 ) (default rule)
I 2019-12-01 19:18:57.103 Backup Interface 172.17.4.151 (255.255.252.0 ) (explicit set)
I 2019-12-01 19:18:57.104 Toolport IP adress 192.168.255.254 (255.255.255.0 )
I 2019-12-01 19:18:57.106 Thread switch log was initiated for 100 entries
I 2019-12-01 19:18:57.106 Thread switch logging is ON
I 2019-12-01 19:18:57.113
I 2019-12-01 19:18:57.114
I 2019-12-01 19:18:57.114 Product : AC 800M PM866
I 2019-12-01 19:18:57.114 Version : 5.1.0/1 (Build 5.1.100.13)
I 2019-12-01 19:18:57.115 Created : 2011-04-17
I 2019-12-01 19:18:57.115 ABB AB
I 2019-12-01 19:18:57.115
I 2019-12-01 19:18:57.116 Controller Reset
I 2019-12-01 19:18:57.123 Position Module Firmware Name Date Version
I 2019-12-01 19:18:57.124 0(L) PM866 FW866 2011-04-17 5.1.100.13
I 2019-12-01 19:18:57.124 OMEGA 2011-04-16 5.1.100.13
I 2019-12-01 19:18:57.124 CPU Unit N/A PM866 C
I 2019-12-01 19:18:57.125 Backplane N/A TP830 B
I 2019-12-01 19:18:57.125 FPGA(17) N/A 1.0/2 B12
I 2019-12-01 19:18:57.126 Support Logic(6:2) N/A 1.0/0
I 2019-12-01 19:18:57.126 CEX Master(1:2) N/A 1.0/3
I 2019-12-01 19:18:57.126 CEX Slave N/A 1.1
I 2019-12-01 19:18:57.127 Modulebus(3:1) N/A 2.0/1
I 2019-12-01 19:18:57.127 CPU Chip N/A 0801
I 2019-12-01 19:18:57.128 RCU(5:0) N/A 2.1/3
I 2019-12-01 19:18:57.128 1 CI854 CI854 OMEGA driver 2004-09-14 02.03
I 2019-12-01 19:18:57.129 FWCI854 PROG 3611540 A 2009-12-01 05.59
I 2019-12-01 19:18:57.129 FWCI854 BOOT 3611539 D 2003-10-20 03.04
I 2019-12-01 19:18:57.129 CI-Unit N/A CI854A PR:J
I 2019-12-01 19:18:57.130 2 Unknown
I 2019-12-01 19:18:57.131 3 CI854 CI854 OMEGA driver 2004-09-14 02.03
I 2019-12-01 19:18:57.131 FWCI854 PROG 3611540 A 2009-12-01 05.59
I 2019-12-01 19:18:57.132 FWCI854 BOOT 3611539 D 2003-10-20 03.04
I 2019-12-01 19:18:57.132 CI-Unit N/A CI854A PR:J
I 2019-12-01 19:18:57.133
I 2019-12-01 19:18:57.133 Actual heapsize: 52872 kBytes
I 2019-12-01 19:18:57.162 Network address is 172.16.4.151, 172.17.4.151.
I 2019-12-01 19:18:57.317 RunMode
I 2019-12-01 19:18:57.370 License Manager: Feature Name Control_Software
I 2019-12-01 19:18:57.370 License Manager: Version 5.1.0
I 2019-12-01 19:18:57.371 License Manager: Hardware ID 00-00-23-0d-9e-54
I 2019-12-01 19:18:57.407 System Initialized.
I 2019-12-01 19:18:57.408 Redirection of Console Channel to System log file 0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
I 2019-12-01 19:19:01.005
I 2019-12-01 19:19:01.005
I 2019-12-01 19:19:01.016 Network Interface 192.168.255.254(255.255.255.0 )
ppp4: ppp 2.1.2 started by
ppp4: Connect: ppp4 <--> /tyCo/0
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.151 is on lo0 but got reply from 00:00:23:0d:9e:54 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.13 is on cpm0 but got reply from a4:1f:72:84:33:76 on cpm1
0xc5e798 (tNetTask):
arp: 172.17.4.151 is on lo0 but got reply from 00:00:23:0d:9e:55 on cpm0
0xc5e798 (tNetTask):
arp: 172.17.4.11 is on cpm1 but got reply from 48:4d:7e:d1:2c:e6 on cpm0
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
I 2019-12-01 19:19:06.555 NSP, Network Storm Protection started,limit = 800 pkt/s
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
I 2019-12-01 19:19:09.366 Hot insert on CEX module number 2 is being performed
I 2019-12-01 19:19:09.646 Position Module Firmware Name Date Version
I 2019-12-01 19:19:09.646 2 CI867 VICIdrv 2010-02-18 7.12
I 2019-12-01 19:19:09.647 FWCI867 2011-04-12 5.1.0111.0
I 2019-12-01 19:19:09.647 FPGA(15) N/A 0.1/0 B0
I 2019-12-01 19:19:09.648 HW revision N/A CI867 C
I 2019-12-01 19:19:09.648 CPU Chip N/A 0700
I 2019-12-01 19:19:09.649 Cirrus 2009-01-16 5.1.0000.0
I 2019-12-01 19:19:09.649 CEM Revcode N/A Unknown (0x00)
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
##############################################
=== Log fetched at 2019-12-04 18:32:45.444 ===
##############################################
(tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.13 is on cpm0 but got reply from a4:1f:72:84:33:76 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.13 is on cpm0 but got reply from a4:1f:72:84:33:76 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.13 is on cpm0 but got reply from a4:1f:72:84:33:76 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.13 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.13 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.12 is on cpm0 but got reply from 00:e0:4d:1a:00:19 on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.11 is on cpm0 but got reply from a0:36:9f:af:00:8f on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
0xc5e798 (tNetTask):
arp: 172.16.4.14 is on cpm0 but got reply from a4:1f:72:81:9d:4b on cpm1
Add new comment