Does IAC (between two PCS controllers) work in system version 5.1 FP3 when using multiple soft controller tool?
System version: 5.1 FP3
Multiple soft controllers instances installed. On two PCS controllers hardware was simulated and IAC communication was checked. The IN direction communication variable times out (errror code: 16#20000). However, the communication variables are resolved.
The MMS communication seems to work fine between the soft controllers.
Multiple soft controllers instances installed. On two PCS controllers hardware was simulated and IAC communication was checked. The IN direction communication variable times out (errror code: 16#20000). However, the communication variables are resolved.
The MMS communication seems to work fine between the soft controllers.
Answers
Make sure you include the MMS Process Number. Auto resolution of the address probably wont work.