AB FlexIO and AC800M with Profibus CI854 Integration
Hello, Team.
Currently, we are working on a project that required the integration of AB FlexIO with AC800M with Profibus CI854.
So far we have downloaded the GSD for the AB Profibus adapter Serie A (also tried serie B), created the hardware library (or some sort of lib) and IO devices using Control Builder M Professional. We have instantiated the library in the hardware tree and downloaded to the controller. However, the unit status of the PB adapter still displaying Configuration data fault, connection down after download completed and all instances have a red triangle (see attachments).
We have checked all the connections, including cables and terminations. Reviewed AB manuals to verify we are not missing anything. Also, we used the CI854 web server and it seems that the slave is reachable but nothing is displayed in the CBM.
800xA Hardware:
PM864A
CI854A
sv6.0.3-2
AB Hardware:
AB Flex I/O Profibus - 24VDC Adapter 1794-APBDPV1 Serie A
AB Flex I/O - Analog Combo 1794-IE4X0E2
AB Flex I/O - 24VDC Sink Input 1794-IB16
Is there any special modification that we need to do in the GSD file and/or during the HW library creation to get this communication established? Any consideration that we need to be aware of to get this library to work? Is there any ABB manual that explains how to use the Wizard tool (just in case we are missing something)?
Many thanks in advance.
Currently, we are working on a project that required the integration of AB FlexIO with AC800M with Profibus CI854.
So far we have downloaded the GSD for the AB Profibus adapter Serie A (also tried serie B), created the hardware library (or some sort of lib) and IO devices using Control Builder M Professional. We have instantiated the library in the hardware tree and downloaded to the controller. However, the unit status of the PB adapter still displaying Configuration data fault, connection down after download completed and all instances have a red triangle (see attachments).
We have checked all the connections, including cables and terminations. Reviewed AB manuals to verify we are not missing anything. Also, we used the CI854 web server and it seems that the slave is reachable but nothing is displayed in the CBM.
800xA Hardware:
PM864A
CI854A
sv6.0.3-2
AB Hardware:
AB Flex I/O Profibus - 24VDC Adapter 1794-APBDPV1 Serie A
AB Flex I/O - Analog Combo 1794-IE4X0E2
AB Flex I/O - 24VDC Sink Input 1794-IB16
Is there any special modification that we need to do in the GSD file and/or during the HW library creation to get this communication established? Any consideration that we need to be aware of to get this library to work? Is there any ABB manual that explains how to use the Wizard tool (just in case we are missing something)?
Many thanks in advance.
Answers
Hi,
By seeing the Images provided, CFG_DATA and CFG_DATA presently active in slave must exactly match then only the data exchange will be happen and the salve will show healthy in CBM.
Actions to be taken,
By using the Data exchange file (.pdf) from AB drive try to configure GSD file again and do communication.
By seeing the Images provided, CFG_DATA and CFG_DATA presently active in slave must exactly match then only the data exchange will be happen and the salve will show healthy in CBM.
Actions to be taken,
By using the Data exchange file (.pdf) from AB drive try to configure GSD file again and do communication.