Connection lost alarm keep on coming when even if the MBConect is disable for CI867
800xa 6.0.3 with Modbus TCP. How to get rid of Connection lost system alarm as it keep on coming when MBConnect is disable( Modbus TCP -CI867)
Alarm is activating and its getting resetted by it self, which fill entire system event list as these alarm are generated in seconds.
Is there any way to disable the alarm ( any setting in the communication cards), as these are system generated alarms ?
Screenshot is attached
Alarm is activating and its getting resetted by it self, which fill entire system event list as these alarm are generated in seconds.
Is there any way to disable the alarm ( any setting in the communication cards), as these are system generated alarms ?
Screenshot is attached
Answers
Hello,
Try disable hardware alarms from controller settings and download.
Check if any alarm expression and if so stop soft alarm service for temporary fix.
Once all ok redo the settings
Try disable hardware alarms from controller settings and download.
Check if any alarm expression and if so stop soft alarm service for temporary fix.
Once all ok redo the settings
Add new comment