AF100 Fieldbus Module warning on system 800xA 6.0.1
Hello Jan-Erik,
I have raised a Support Case #20190925-1537780 to Local Support Line (Singapore) but take too long to receive the information/solution for that. So I post it here to get your support or other experts can help.
I brief Support case as below
=======================================
![]()


I used ONB to check AF100 item:
I have raised a Support Case #20190925-1537780 to Local Support Line (Singapore) but take too long to receive the information/solution for that. So I post it here to get your support or other experts can help.
I brief Support case as below
=======================================
In my system 800xA ver 6.0.1, I have received these messages from System message (attached screenshot),
I used ONB to check AF100 item:
- WARN = 1
- ERR = 0
- DIAG = SE (both modules)
There is no any system message from ONB for this node.
The operation is still working.
*** No any modification on the hardware/software of CI522.
=============================================================
Thank you for your support.
Rgds,
Vu,
Answers
Your highlighted error is "b 1 s 2 p 11" i.e. Bus 1 Station 2 Position 11, but you haven't shown that module in your screenshot.
Is there an error on that module?
Is there an error on that module?
Hello Vu.
What is the AC450 AF 100 station number ?
Is it 79 ?
When using Redundant CI522 boards in the AC450 the AF100 station number must be 5 or below, else you may get cosmetic warnings in the
AC450 system status display in 800xA or AS500 OS
Best Regards
Jan-Erik
What is the AC450 AF 100 station number ?
Is it 79 ?
When using Redundant CI522 boards in the AC450 the AF100 station number must be 5 or below, else you may get cosmetic warnings in the
AC450 system status display in 800xA or AS500 OS
Best Regards
Jan-Erik
The AF100 manual says
When redundant CI522s and CI820s are used on the bus, then one of the following rules must be followed:
– The redundant CI522 pair must be assigned a station number lower than five (5). – Two master defined communication interfaces must be assigned station numbers lower than five (5).
One side effect when using station number 5 or higher is a not properly working system status for the CI522 boards.
It is very easy to change the CI522 board station number from 79 to 1 but, then if station 1 exists on the bus, you must
change that station number and all I/O boards to a higher not used station number.
Econfig mode is required.
BR Jan-Erik
When redundant CI522s and CI820s are used on the bus, then one of the following rules must be followed:
– The redundant CI522 pair must be assigned a station number lower than five (5). – Two master defined communication interfaces must be assigned station numbers lower than five (5).
One side effect when using station number 5 or higher is a not properly working system status for the CI522 boards.
It is very easy to change the CI522 board station number from 79 to 1 but, then if station 1 exists on the bus, you must
change that station number and all I/O boards to a higher not used station number.
Econfig mode is required.
BR Jan-Erik