Upgrade System800xA 6.03 to 6.1
Hi everyone,
Currently, I am conducting tests prior to the upgrade System800xA 6.03 to 6.1, but, when the update is being carried out in the other nodes, except in the aspects one, this error appears, that attaching in the image.
Media is running Aspect Server.
I hope you can help me.
Currently, I am conducting tests prior to the upgrade System800xA 6.03 to 6.1, but, when the update is being carried out in the other nodes, except in the aspects one, this error appears, that attaching in the image.
Media is running Aspect Server.
I hope you can help me.
Voted best answer
It seems that you have 800xA Services not running and therefore there is a timeout (for each 800xA Services not running) of 3600 seconds (i.e. 1 hour).
You will have to wait for the timeout before you can "Manually resolve..." the issue (800xA Services not running).
I hope the above might help you
BR Carsten