Cpu
Hey all
I have pm564 eth cpu and my problem that in automation builder the digital input for example di5 when I make online in automation builder the status is true but in codsys its false when I change the name in mapping list and run again the codsys its work , so what I miss !!!
I have pm564 eth cpu and my problem that in automation builder the digital input for example di5 when I make online in automation builder the status is true but in codsys its false when I change the name in mapping list and run again the codsys its work , so what I miss !!!
Answers
Hi,
Check if there is no duplicate of variable declaration.
The variable, used in mapping, have to be declared only in Resources -> Global Variables -> IO_Bus... or ONBIO..., nowhere else.
Use Global Search,,, to check that.
Check if there is no duplicate of variable declaration.
The variable, used in mapping, have to be declared only in Resources -> Global Variables -> IO_Bus... or ONBIO..., nowhere else.
Use Global Search,,, to check that.
Add new comment