800xA 6.0.3, Information Manager alarm list
We use 800xA 6.0.3 with Information Manager. Events generate by AlarmCond or SimpleEventDetector in AC800M controller.
When Event is generating with system timestamp it works normally and we can find it in 800xA and IM Alarm Lists.
When we are using external timestamp and time for example 1 day before system time, message exist in 800xA alarm list, but don’t appear in IM alarm list.
Is any possibility to force send message in IM Event List?
Voted best answer
Isn't the purpose of the external timestamp to read time from SOE IO?
The SOE IO modules are synced via the module bus and should be in sync with the controller.
I believe the IM message log require events to arrive in time order; expecting one day old events sound strange to me...
The SOE IO modules are synced via the module bus and should be in sync with the controller.
I believe the IM message log require events to arrive in time order; expecting one day old events sound strange to me...