ABB ACS880 Driver Excessive Temperature Fault code 4310
I would like to seek your kind assistance to rectify our ABB Inverter model ABB ACS880-01-206A-3 Driver Excessive Temperature showing fault code 4310.
We already have try all the solution recommended in manual.
We already have try all the solution recommended in manual.
- Check all ambient conditions.
- Check air flow and fan operation.
- Check heat sink fins and blow all the dust pick ups.
- Check motor power against drive power.
Answers
Hi
if you have already checked the solutions recommended in the manual, in my opinion you have no choice but to contact the nearest ABB service, because you will have to open the drive and potentially replace some sensor - which is probably broken - or a sensor interface card itself.
BR
Flavio
if you have already checked the solutions recommended in the manual, in my opinion you have no choice but to contact the nearest ABB service, because you will have to open the drive and potentially replace some sensor - which is probably broken - or a sensor interface card itself.
BR
Flavio