IPConfig Serial Port Configuration
To use IPConfig, what should the Serial Port configuration be: Baud Rate,Data bits, Parity, Stop bits. I have looked but not able to find in manual.
Answers
Hi,
You don't have to configure COM4 port - it is service port for service tools.
Connect TK212 to it and press INIT button. IPConfig tool should detect the CPU
You don't have to configure COM4 port - it is service port for service tools.
Connect TK212 to it and press INIT button. IPConfig tool should detect the CPU
Hi again,
From CBM help, click on COM4 and press F1:
"Default Tool Port Settings:
9600
parity: none
data bits: 8
stop bits:1
flow control: none
Delay of the RTS signal:0
Parameter values for the Tool Port are predefined to the value in the table above and cannot be changed"
From CBM help, click on COM4 and press F1:
"Default Tool Port Settings:
9600
parity: none
data bits: 8
stop bits:1
flow control: none
Delay of the RTS signal:0
Parameter values for the Tool Port are predefined to the value in the table above and cannot be changed"
Source: CBM Help -> F1