AC800M PM866 primary & secondary both controller failure while downloading new logic
Redundant controller AC800M PM866 went into fault status while the modbus program was downloaded.
Answers
Check the firmware version
By navigate
Right click on controller >>remote system >> show firmware version.
By navigate
Right click on controller >>remote system >> show firmware version.
What was the logic change?
Looks like there was a fault generated during the download and the Modbus card is not responding or faulty, this in-turn has halted the controller and the OPC service.
Physically check the status of the card, if in fault remove and re-insert and check if the fault clears.
Contact or raise a support request with log files.
Looks like there was a fault generated during the download and the Modbus card is not responding or faulty, this in-turn has halted the controller and the OPC service.
Physically check the status of the card, if in fault remove and re-insert and check if the fault clears.
Contact or raise a support request with log files.