Freelance 2019 Installation Errors
A site has upgraded from Freelance 2013 to Freelance 2019. Now there are 2 errors, the first stating
"You configured more monitors than licensed.
Freelance Operations will now go into Emergency mode.
It will become unusable and shut down in 100 days."
The license have been upgraded and digivis licenses are the same as before. Number of configured monitors have not changed.
The second error states:
"Error in Freelance Operations watchdog .
Check event log for details."
Voted best answer
Hi,
The 1st error comes because of, number of monitor configured on the operator station are more than the license what you have.
Make sure your operator station license has string called "MULTIMONITOR,11,1,*4". 4-Indicates the maximum number of monitor allowed on one operator station.
If the string is not available then only one monitor is allowed by default.
Multimonitor feature supports you to connect maximum 4 monitors with one operator station PC.
This can be configured on header of VIS node(operator station).
1. Right click on VIS node-> Header-> Cofigure monitor
Change the configuration as per your license, eg: if you have license with *4 then change "Configured monitors as 4"
2nd error may be because of 1st one.
Add new comment