E2 054 Error on AC500. Cant run program after login
Hi
After migration to Automation Builder 2.2 cant run the program. Controller Login and Download the program, but on PLC screen shows error E2 054 and doesnt run
On the CPU diagnosis page this error doesnt nave any description (see attached screenshot)
Please help, already spend whole day to fix it, but no success
Thanks
After migration to Automation Builder 2.2 cant run the program. Controller Login and Download the program, but on PLC screen shows error E2 054 and doesnt run
On the CPU diagnosis page this error doesnt nave any description (see attached screenshot)
Please help, already spend whole day to fix it, but no success
Thanks
Answers
Hi,
The help file contains no specific information about the E2 error (Serious error). I can only suggest the following.
1) Clear errors from the error buffer
2) Recreate configuration data via context menu of the Codesys program in Automation Builder
3) Clean ALL>> Rebuild ALL >> Download program >> Create Boot project >> From PLC Browser execute 'reboot' >> Login and set PLC in RUN mode
Regards
Rahil
The help file contains no specific information about the E2 error (Serious error). I can only suggest the following.
1) Clear errors from the error buffer
2) Recreate configuration data via context menu of the Codesys program in Automation Builder
3) Clean ALL>> Rebuild ALL >> Download program >> Create Boot project >> From PLC Browser execute 'reboot' >> Login and set PLC in RUN mode
Regards
Rahil