AC500 hold last stat when communication is lost
Dear All,
who to configure ac500 so that the remote DO hold their last state in case of communication loss between the plc and the Interface module.
who to configure ac500 so that the remote DO hold their last state in case of communication loss between the plc and the Interface module.
Answers
Hi,
An S500 DO module has a parameter called 'Behaviour outputs at comm. error' located in the DO module's DOxxx Parameters tab window. Use the drop down list under Value column and select 'Last Value' as shown in the below image.

Regards
Rahil
An S500 DO module has a parameter called 'Behaviour outputs at comm. error' located in the DO module's DOxxx Parameters tab window. Use the drop down list under Value column and select 'Last Value' as shown in the below image.
Regards
Rahil