AC 800F replaced a new PM-803F not work
Hi,
There is a question for AC800F. The PM-803F of AC800F is not worked ,so i buy a new one replace it.But still i install the new PM-803F,and load the operating system, the equipment is also not work.There are two question: one is the LED light of SA 811F is in off state;the other is both of the LED light in FI 830F is off state.Please give me some help.

The question is in this Figure
Best regards.
There is a question for AC800F. The PM-803F of AC800F is not worked ,so i buy a new one replace it.But still i install the new PM-803F,and load the operating system, the equipment is also not work.There are two question: one is the LED light of SA 811F is in off state;the other is both of the LED light in FI 830F is off state.Please give me some help.

The question is in this Figure
Best regards.
Answers
Hi
Please check below
Is the controller firmware is updated from current running CBF machine?
Check the profibus communication module (FI830F) also updated from CBF, verify the versions of old running controller and new one.
Also share the some screen shot of CBF in commissioning mode & controller logs
Regards
Subramani TN
Please check below
Is the controller firmware is updated from current running CBF machine?
Check the profibus communication module (FI830F) also updated from CBF, verify the versions of old running controller and new one.
Also share the some screen shot of CBF in commissioning mode & controller logs
Regards
Subramani TN
I once had the same problem, and the existing controller had been loaded with a certain Freelance software version including a software roll-up years ago. In the meantime, the engineering station had died and was replaced, but the roll-up had not been installed again. The controller that had to be replaced was now loaded with the same Freelance software *without* the roll-up and it couldn't sync itself to the running controller.
So I'd try checking the Software versions on the controller's diagnostic page. It should look something like this:
Software Versions:
BootLoader: 10.30 [9142]
Runtime System: 10.35
HW Selftest: F04.102.00
The bootloader and runtime system versions need to agree on both controllers.
If they don't, you'll probably need to figure out which Freelance version and roll-ups were used on the running controller.
Alternatively, connect the serial diagnostic cable to the replaced controller and observe the bootstrapping.
So I'd try checking the Software versions on the controller's diagnostic page. It should look something like this:
Software Versions:
BootLoader: 10.30 [9142]
Runtime System: 10.35
HW Selftest: F04.102.00
The bootloader and runtime system versions need to agree on both controllers.
If they don't, you'll probably need to figure out which Freelance version and roll-ups were used on the running controller.
Alternatively, connect the serial diagnostic cable to the replaced controller and observe the bootstrapping.
In your picture, it looks like you have only interconnected
the both FI830.
In this case, it is not possible to get both controller in sync state, you have to
connect at least one configured profibus slave or you have to disable both
FI830 cards.
Best regards
the both FI830.
In this case, it is not possible to get both controller in sync state, you have to
connect at least one configured profibus slave or you have to disable both
FI830 cards.
Best regards