How to solved abnormal OPCDAConnector Status Initialize ?
Dear Team,
We have problem with OpcDAConnector that status is "initialize" check on Engineering Workplace/Service Structure (on AFW service monitoring its color "yellow") while the other OpcDAconnector was in good condition (in "service" state).
I realize the problem due to IT Control Connection (ABB.Shadow.OPCServer) was bad quality.
How to solve this?
Kindly please advise
Thanks :)
We have problem with OpcDAConnector that status is "initialize" check on Engineering Workplace/Service Structure (on AFW service monitoring its color "yellow") while the other OpcDAconnector was in good condition (in "service" state).
I realize the problem due to IT Control Connection (ABB.Shadow.OPCServer) was bad quality.
How to solve this?
Kindly please advise
Thanks :)
Answers
The OPC DA Connector service require the OPC server to expose "OPC_STATUS_RUNNING" status for the connector to enter "Service" state.
You can probe the OPC server using advdsopcclient.exe tool. Browse, connect and check status.
If the ABB.Shadow.OPCServer (PNSM) is unhealthy you must find what is wrong.
Did it ever work on this computer?
You could try to reinstall the software if you have media.
I suggest that you file a support case with your regional ABB support organization for assistance.
You can probe the OPC server using advdsopcclient.exe tool. Browse, connect and check status.
If the ABB.Shadow.OPCServer (PNSM) is unhealthy you must find what is wrong.
Did it ever work on this computer?
You could try to reinstall the software if you have media.
I suggest that you file a support case with your regional ABB support organization for assistance.
Hello,
Ensure you have selected the PNSM node is selected, check data source def and always try do the propagate from the PNSM node only
Ensure you have selected the PNSM node is selected, check data source def and always try do the propagate from the PNSM node only