800xA Operator Issue
If I login with 800xA service then SCADA Is communicating with redundunt servers but If I login with Operator Login It is not communicating. Earlier It was working but suddenly this happens so suggest how to solve it.
Voted best answer
Account must be:
- enabled
- have a not expired password
- be member of IndustrialITUser group
- be properly added to System 800xA User Structure
When using Windows for Workgroups, each of the above settings (except the last) must be checked in each computer. Additionally, password synchronization in a workgroup is a manual effort (must be set exactly same in all members of the workgroup).
- enabled
- have a not expired password
- be member of IndustrialITUser group
- be properly added to System 800xA User Structure
When using Windows for Workgroups, each of the above settings (except the last) must be checked in each computer. Additionally, password synchronization in a workgroup is a manual effort (must be set exactly same in all members of the workgroup).
Answers
Does the password never change is activated ? Are you able to login in all the machine with the operator account. Workgroup or domain ?