AC450 CF Card Write error
1. AC450 (PM511) dump is taken, got 7 .AD files
2. When writing to Flash card, writes up to 6th file 50% and gives error. (this is identified from the DOS window which counts from 0 to 100% for each file)

3. 10MB Flash card is used for writing. Same sized cards are used in other Units and is working.
What could be the problem, a programming error or something else?
2. When writing to Flash card, writes up to 6th file 50% and gives error. (this is identified from the DOS window which counts from 0 to 100% for each file)

3. 10MB Flash card is used for writing. Same sized cards are used in other Units and is working.
What could be the problem, a programming error or something else?
Answers
Hello.
Which version of Control Builder A are you using ?
Have you programmed PCMCIA cards with as many and large DUAP files before on one card ?
Maybe you are affected by a bug in an older version of CBA ?
If I remember right wi don't split the DUAP in smaller files in later versions of CBA.
Best Regards
Jan-Erik
Which version of Control Builder A are you using ?
Have you programmed PCMCIA cards with as many and large DUAP files before on one card ?
Maybe you are affected by a bug in an older version of CBA ?
If I remember right wi don't split the DUAP in smaller files in later versions of CBA.
Best Regards
Jan-Erik
Add new comment