800xA V6 One Slow Graphic
Hi... I have an 800xA v6.0.3 system, 800M Connect. There is one graphic that can take several seconds to come up. When opening a faceplate from that graphic, the faceplate may take several seconds to fully display.
I have run the diagnostics, consistency checker, and reference tool on that graphic display aspect. I've confirmed all object names on that display are unique. I can't find anything different about this display from all the others in this system, which are all working fine.
Any suggestions? Thanks...
I have run the diagnostics, consistency checker, and reference tool on that graphic display aspect. I've confirmed all object names on that display are unique. I can't find anything different about this display from all the others in this system, which are all working fine.
Any suggestions? Thanks...
Answers
Are you using _width or _height with an aspect view wrapper. I notice that this will cause the graphic to redraw continuously. If so, try -1. Are you using Out terminal variable that are used to do some actions in the graphic that could create a loop. Last thing, in your copy you delete half of the symbol until it’s working that you undo your last delete to find what in the graphic is causing this. Is it doing this on different machine ? Maybe you local cache graphic version is corrupt. i would be curious to restore your backup on our test bench to see if your 800xA database is healthy.
by backdraft
Some more information (screenshot of diagnostic) or even an export of the display and dependencies may be required to help...
by Boris Rank: 49 on 9/10/2019 2:04:17 AM | Like (0) | Report
Make sure to remove all animations or VB scripts which you may have.
by elemravi Rank: 33 on 9/12/2019 7:18:15 AM | Like (0) | Report
Lots of late binding connections ??
Make a copy of this display. Does the copy also behave same way?
Add new comment