IO configuration on ControlBuilder
Good Morning.
I have an Control Builder ver. 5.0.2. I must insert (and configure) new DI/DO cards 818 in the configuration, but i can't find on the hardware libraries. (ModulesHwLib 1.1.6).
The library can only be upgraded (and if so, how) or the entire CB must be updated?
Thanks for the tips
I have an Control Builder ver. 5.0.2. I must insert (and configure) new DI/DO cards 818 in the configuration, but i can't find on the hardware libraries. (ModulesHwLib 1.1.6).
The library can only be upgraded (and if so, how) or the entire CB must be updated?
Thanks for the tips
Answers
Greetings,
If you are using Profibus for IO communication, you can use new GSD file for S800 IO Cards.
You can import and customize new cards for your needs.
You can find GSD ile in ABB Library.
Hope it helps.
If you are using Profibus for IO communication, you can use new GSD file for S800 IO Cards.
You can import and customize new cards for your needs.
You can find GSD ile in ABB Library.
Hope it helps.
Hi,
As far I know DI818 is included in Compact Control Builder starting from version 5.1.1
Upgrade procedure is described in 3BSE041584-511, look also for revision index documents for CCB M
As an example, I checked in CCB ver. 5.1.0/1 and the module DI818 is not presented (S800IoModulenusHwLib 1.1-10)
As far I know DI818 is included in Compact Control Builder starting from version 5.1.1
Upgrade procedure is described in 3BSE041584-511, look also for revision index documents for CCB M
As an example, I checked in CCB ver. 5.1.0/1 and the module DI818 is not presented (S800IoModulenusHwLib 1.1-10)
Add new comment