Analog Output of ACS550 VFD
Dear All,
I want to get 4-20mA as Speed Feedback from ACS550 to DCS.
I have set following parameters but 4-20mA is not coming from VFD. Please help whether there is any error of my parameter.
Parameters
1501 - AO1 Content Sel - Speed
1502- AO1 Content Min- 0 RPM
1503 - AO1 Content Max - 1500 RPM
1504 - Min AO1 - 4.0 mA
1505- Max AO1 - 20 mA
1506 - Filter AO1 - 0.1S
AO is not directly connected to any Analog RPM meter. This 4-20mA value will be used as AI signal in PLC.
Please assist me.
Regards,
SS
I want to get 4-20mA as Speed Feedback from ACS550 to DCS.
I have set following parameters but 4-20mA is not coming from VFD. Please help whether there is any error of my parameter.
Parameters
1501 - AO1 Content Sel - Speed
1502- AO1 Content Min- 0 RPM
1503 - AO1 Content Max - 1500 RPM
1504 - Min AO1 - 4.0 mA
1505- Max AO1 - 20 mA
1506 - Filter AO1 - 0.1S
AO is not directly connected to any Analog RPM meter. This 4-20mA value will be used as AI signal in PLC.
Please assist me.
Regards,
SS
Answers
Hi,
Your settings seems OK. So you have to measure at least 4 mA to AO1 = X1: 7 and 9 if drive is stopped (speed=0) AND your AO is OK
You can try with setting 1501=107 or 110 in order to have some values different from 0
Your settings seems OK. So you have to measure at least 4 mA to AO1 = X1: 7 and 9 if drive is stopped (speed=0) AND your AO is OK
You can try with setting 1501=107 or 110 in order to have some values different from 0