How to diagnose AO810V2 module warning
Warning led is active on all of the Analogue output modules AO810V2 .
What are the steps to diagnose this issue, I have looked at the manual for this module and it mentions only that it could be a external or internal channel fault.
What are the steps to diagnose this issue, I have looked at the manual for this module and it mentions only that it could be a external or internal channel fault.
Voted best answer
Greetings,
Did you check channel diagnostics?
Maybe open circuit cause this warning led.
Hope it helps.
Did you check channel diagnostics?
Maybe open circuit cause this warning led.
Hope it helps.
Answers
The manual says:
The WARNING (yellow) LED indicates that there is some kind of process error such as an open circuit, or power supply fault.
I would check the 24 volt and fuse(s) as you have the problem on all channels.
BR Jan-Erik
The WARNING (yellow) LED indicates that there is some kind of process error such as an open circuit, or power supply fault.
I would check the 24 volt and fuse(s) as you have the problem on all channels.
BR Jan-Erik
I have checked the diagnostics and channel 8 has an error indicated.
Attached screen shots of diagnostics and browse showing the error.
Attached screen shots of diagnostics and browse showing the error.
Should all unused channels be set to deactivated in the configuration to remove these module warnings?
All unused channels should be deactivated as any single "open circuit" channel will cause the module Warning led to be active.