Hello sir,i need a help in S800 IOS configuration in Advant Controller 450 AC450 PM510V08.
sir, i am totally new in DCS advant controller 450. kindly give me support how we will configure S800 IOs module in AC450 PM510V08 and what are the supporting software for AC450 PM510V08.
Voted best answer
Hello,
You need to have CI522 card in AC450 controller, and TC516 modem is requited to communication of S800 IO with AC450 controller,
This communication is called AF100 communication, You need to establish AF100 communication between AC450 and remote IO called S800 IO's
You need to have CI522 card in AC450 controller, and TC516 modem is requited to communication of S800 IO with AC450 controller,
This communication is called AF100 communication, You need to establish AF100 communication between AC450 and remote IO called S800 IO's
Answers
Hello Sir.
First of all you need a system software that support S800 I/O. First generation of AC450 with PM510 CPU software version 7.0/* does not support S800 I/O.
If used you need to upgrade to latest SW*9.0/* for PM510 CPU SW* 8.0 is also working but is not recommended since it's the very first version with many software bugs.
AF100 interface board CI522 was not supported in the versions of AC450 with PM510 CPU, You need the old CI520V1 AF100 inteface board when using PM510 CPU.
In general we strongly recommend to upgrade all old AC450 with PM510 CPU to current active sales version with new PM511V16 CPU and latest system software from December 2016 for best functionallity. This latest software version also support the in active sales Ci522A AF100 interface board. ( CI520V1 is limited life cycle)
Read the Advant Fieldbus 100 users guide for the Advant Fieldbus HW & SW implementation, this is a quite easy task.
Finally you must re-dimension the database for AF100 and S800 IO boards and create the CI520 or CI522 AF100 interface boards the CI810/820 IO stations and the S800 IO boards you need.
Then you can create the CI522 DB element, the CI810/820 IO stations and the S800 I/O boards using CRDB or load them via source code.
Best Regards Jan-Erik
First of all you need a system software that support S800 I/O. First generation of AC450 with PM510 CPU software version 7.0/* does not support S800 I/O.
If used you need to upgrade to latest SW*9.0/* for PM510 CPU SW* 8.0 is also working but is not recommended since it's the very first version with many software bugs.
AF100 interface board CI522 was not supported in the versions of AC450 with PM510 CPU, You need the old CI520V1 AF100 inteface board when using PM510 CPU.
In general we strongly recommend to upgrade all old AC450 with PM510 CPU to current active sales version with new PM511V16 CPU and latest system software from December 2016 for best functionallity. This latest software version also support the in active sales Ci522A AF100 interface board. ( CI520V1 is limited life cycle)
Read the Advant Fieldbus 100 users guide for the Advant Fieldbus HW & SW implementation, this is a quite easy task.
Finally you must re-dimension the database for AF100 and S800 IO boards and create the CI520 or CI522 AF100 interface boards the CI810/820 IO stations and the S800 IO boards you need.
Then you can create the CI522 DB element, the CI810/820 IO stations and the S800 I/O boards using CRDB or load them via source code.
Best Regards Jan-Erik
by Jan-Erik Rask Rank: 81 on 8/22/2019 1:13:06 AM | Like (0) | Report
Hello Sir.
First of all you need a system software that support S800 I/O. First generation of AC450 with PM510 CPU software version 7.0/* does not support S800 I/O.
If used you need to upgrade to latest SW*9.0/* for PM510 CPU SW* 8.0 is also working but is not recommended since it's the very first version with many software bugs.
AF100 interface board CI522 was not supported in the versions of AC450 with PM510 CPU, You need the old CI520V1 AF100 inteface board when using PM510 CPU.
In general we strongly recommend to upgrade all old AC450 with PM510 CPU to current active sales version with new PM511V16 CPU and latest system software from December 2016 for best functionallity. This latest software version also support the in active sales Ci522A AF100 interface board. ( CI520V1 is limited life cycle)
Read the Advant Fieldbus 100 users guide for the Advant Fieldbus HW & SW implementation, this is a quite easy task.
Finally you must re-dimension the database for AF100 and S800 IO boards and create the CI520 or CI522 AF100 interface boards the CI810/820 IO stations and the S800 IO boards you need.
Then you can create the CI522 DB element, the CI810/820 IO stations and the S800 I/O boards using CRDB or load them via source code.
Best Regards Jan-Erik