Simulate IAC MMS
How to simulate the IAC MMS protocol ?
I tried to use the simulate hardware settings and ABB soft controller. But the hardware 0.5 (IP - IAC MMS) not getting simulated.
How to resolve this issue ? I am using inter application communication
Getting the error while trying to download the application to the soft controller
"Error 9096 : FG1 : HW The communication protocol in connected library for IAC MMS at position 0.5.1 is invalid"
Any suggestion appreciable.
I tried to use the simulate hardware settings and ABB soft controller. But the hardware 0.5 (IP - IAC MMS) not getting simulated.
How to resolve this issue ? I am using inter application communication
Getting the error while trying to download the application to the soft controller
"Error 9096 : FG1 : HW The communication protocol in connected library for IAC MMS at position 0.5.1 is invalid"
Any suggestion appreciable.
Answers
How is the hardware configured ? Are you using a PM8** with the "Simulate Hardware" setting enabled ? ( Sorry, I don't have a system available to test, but from memory I think you cant define the controller as a "softController" )
Be aware that MMS isnt "simulated" - it actually runs. This means enabling MMS in a simulated controller connected to a real plant will communicated with that real plant.
Be aware that MMS isnt "simulated" - it actually runs. This means enabling MMS in a simulated controller connected to a real plant will communicated with that real plant.