Undefined Service in redundant ASCS 152
Hi Guys
i work with v.5.0.1 AC800M after several power failure due to our downtime i try to restart our ASCS152 (we have 2 ASCS(ASCS 152&153)) one of them starts with all Green But the other all service enable But Undefined.
now downtime is over and system is running how can i fix this without disturbing process
thanks in advance.
i work with v.5.0.1 AC800M after several power failure due to our downtime i try to restart our ASCS152 (we have 2 ASCS(ASCS 152&153)) one of them starts with all Green But the other all service enable But Undefined.
now downtime is over and system is running how can i fix this without disturbing process
thanks in advance.
Answers
Hi!
The resolution on your pics are not good enough to see details...
I guess you've tried several restarts?
Probably network related, check network cabling, status (RNRP), including logs.
Could there be a network device that lost configuration after the power failure (port config/VLAN etc)?
BR
The resolution on your pics are not good enough to see details...
I guess you've tried several restarts?
Probably network related, check network cabling, status (RNRP), including logs.
Could there be a network device that lost configuration after the power failure (port config/VLAN etc)?
BR
I see you have disconnected and non functioning network cards. This can sometimes cause problems with RNRP binding to IP addresses that don't work and prevent your system from starting properly.
You should resolve these Network issues or disable network cards that are not required. In any case, unused network cards must NOT use IP addresses that are automatically configured by RNRP.
You should resolve these Network issues or disable network cards that are not required. In any case, unused network cards must NOT use IP addresses that are automatically configured by RNRP.
Add new comment