using pm866 controller on 800xa 5.0
hi,
is it possible to use pm866 controller with 800xa 5.0 ?
is it possible to use pm866 controller with 800xa 5.0 ?
Answers
Hi,
Please refer this Below Documents as per revision for Controller Hardware with respective to 800xA version.
Please refer this Below Documents as per revision for Controller Hardware with respective to 800xA version.
Version
Document no
800xA 5.0
3BSE036351R5001
800xA 5.0 SP1
3BSE036351R5011
800xA 5.0 SP2
3BSE036351R5021
Supported controllers are included only in the base software releases or feature packs. You cannot add another controller type later. Eg. PM891 support starts at version 5.1 and cannot be added into earlier versions.
The easiest way to see if a controller is supported i your system is to open control builder and try to add a new controller. All supported hardware is listed.
The easiest way to see if a controller is supported i your system is to open control builder and try to add a new controller. All supported hardware is listed.
hi,
please share the exact snapshot of the system version details.
You can Use PM866 in 5.0 SP1 , PM86 has 1.4 times better performance then PM864 and its switch over time is also much lesser.
please refer the attached image of PM866 Sales product release document.
please share the exact snapshot of the system version details.
You can Use PM866 in 5.0 SP1 , PM86 has 1.4 times better performance then PM864 and its switch over time is also much lesser.
please refer the attached image of PM866 Sales product release document.
Hi!
The PM866 controller was released in 2008 and is supported by system version 5.0.1/1.
However:
I would rather consider a system upgrade (ver 6.x) since you are running an obsolete operating system.
If not, consider fixes available for these out-of-support versions of Windows in KB4500705
BR
Add new comment