Process Panel 800 External OPC server with AC500
Dear colleagues
I'm working on a project where I have to connect PP877 with AC500 plc using Codesys OPC DA Classic. When I simulate the Scada in Panel Builder 800 on my PC everything works fine. The codesys OPC server is installed locally on my PC. But when I download the Scada software to the real PP877 then I have no connection. On the Panel Builder I choose OPC Classic Server with remote option because the codesys OPC server is installed on my PC. I know that I have to configure DCOM settings in order for this to work but I can't do that on PP877 because I have no access to the operating system.
Can you help?
I'm working on a project where I have to connect PP877 with AC500 plc using Codesys OPC DA Classic. When I simulate the Scada in Panel Builder 800 on my PC everything works fine. The codesys OPC server is installed locally on my PC. But when I download the Scada software to the real PP877 then I have no connection. On the Panel Builder I choose OPC Classic Server with remote option because the codesys OPC server is installed on my PC. I know that I have to configure DCOM settings in order for this to work but I can't do that on PP877 because I have no access to the operating system.
Can you help?
Voted best answer
Greetings,
OPC server is available only when you are using PC Based clients.

For more detail please refer to:
https://library.e.abb.com/public/4e3c...
Hope it helps you.
OPC server is available only when you are using PC Based clients.

For more detail please refer to:
https://library.e.abb.com/public/4e3c...
Hope it helps you.