How to generate over current Fault alarm for AI module channel at 22.8mA?
Answers
I think you with the simulate hardware feature can enter a IO-value and make the fault.
Hi,
Look in the help for your AI module:
For analog input modules it is possible to go outside the channel value range of 0-100%, if the Clamp analog in values parameter of the controller hardware object is set to false
For example for AI810 and 4-20mA range:
Look in the help for your AI module:
For analog input modules it is possible to go outside the channel value range of 0-100%, if the Clamp analog in values parameter of the controller hardware object is set to false
For example for AI810 and 4-20mA range:
Signal Range
Output Signal Range
Input Signal Range
4…20 mA
-25…115%
0…22.4 mA