How to invert Output W.e.r Speed Analog input (4 - 20mA)
hi
i have connected Speed ref to AI i.e 4 - 20mA. How i can configure parameter for increasing speed when Analogue input is 4mA and decrease the speed when Analogue input is 20mA
Drive model ACS355
i have connected Speed ref to AI i.e 4 - 20mA. How i can configure parameter for increasing speed when Analogue input is 4mA and decrease the speed when Analogue input is 20mA
Drive model ACS355
Answers
Hi
I don't have the simulator on hand and so I go from my memory .... try to set parameter 13.01 to 100% and 13.02 to 20% - of course if you use AI1 for reference speed.
Do not forget to set the dip switch for AI1 to current, default setting is for Voltage input
BR
Flavio
I don't have the simulator on hand and so I go from my memory .... try to set parameter 13.01 to 100% and 13.02 to 20% - of course if you use AI1 for reference speed.
Do not forget to set the dip switch for AI1 to current, default setting is for Voltage input
BR
Flavio