ACS880 Fault "SSW" 64B1
The drive had a fault the damage the ZINP-571 card once replace with a new on the drive has the following fault:
a- Fault "SSW" 64B1
b- In actual values there is no DC Bus voltage indication 1.11, but drive is Powered and on.
c- The drive is in local mode and panel is active 19.17 (No), but will not accept start command, ref up or down.
d- I would like to re-download the firmware (AINF6 2.62.0.0) in order to discard any corruption of the software that may occur with the initial damage of the ZINP-571, any suggestions...?
a- Fault "SSW" 64B1
b- In actual values there is no DC Bus voltage indication 1.11, but drive is Powered and on.
c- The drive is in local mode and panel is active 19.17 (No), but will not accept start command, ref up or down.
d- I would like to re-download the firmware (AINF6 2.62.0.0) in order to discard any corruption of the software that may occur with the initial damage of the ZINP-571, any suggestions...?
Answers
The measuring of dc volts is carried out by the zint or bint board, you may check that board
BR
BR
Add new comment