CI855 as Clock Master on MB300
Hello.
I have time sync issues.
My system (how I want it):
Controller 1, PM891:
- receives time from SNTP
- sends CNCP-time as CNCP-master 1
- CI855 as MB300 ClockMaster on MB300-net 12
Controller 2, PM864:
- receives CNCP (CNCP-master 0)
- CI855 as MB300 ClockMaster on MB300-net 12
Controller 3, PM866:
- receives CNCP (CNCP-master 0)
- no CI855
Controller 4, PM891:
- receives time from SNTP
- sends CNCP-time as CNCP-master 2
- CI855 as MB300 ClockMaster on MB300-net 11
800xA system 1:
- combined AS/CS
- AC800Connect
- AC400Connect
- RTA CLS1-setting 0,2,0
- Reverse_sync_mode = false
- two AC450, both CLS1-setting 0,2,0
800xA system 2:
- two AS + two CS + IM
- AC800Connect
- AC400Connect
- RTA CLS1-setting 0,2,0
- Reverse_sync_mode = false
- three AC450, all with CLS1-setting 0,2,0
The two 800xA systems are independent from each other.
One Control network for all CS/AC800M in both systems.
One ClientServer network for all AS/CS/Clients in both systems.
MB300 nets 11 and 12 is totally separated.
800xA system 1 works. Time diff between PC:s is < 20ms, and AC800M seems to have the correct time.but AC450 does not seem to receive the correct time.
800xA system 1 does NOT work. When I set CI855 on Controller 1 to be MB300 ClockMaster (on MB300-net 12), nothing happened. I could NOT see that AC450 adopted correct time.
When I set CI855 on Controller 2 to be (second) MB300 ClockMaster, all AC450 (on MB300-net 12) got their clocks set to 1985-07-08/19:49:XX!!!
Is it wrong to have two CI855 as masters on the same MB300?
Book (System 800xA NetworkConfiguration System Version 5.1 3BSE034463-510 E page 16+0) says "it is recommended to use a CI855 in AT LEAST ONE AC800M so that the time can be distributed from the Control Network to MB300 via CI855"
Why wont the AC450's get synced?
Anyone has a clue?
Thanks
/Martin
I have time sync issues.
My system (how I want it):
Controller 1, PM891:
- receives time from SNTP
- sends CNCP-time as CNCP-master 1
- CI855 as MB300 ClockMaster on MB300-net 12
Controller 2, PM864:
- receives CNCP (CNCP-master 0)
- CI855 as MB300 ClockMaster on MB300-net 12
Controller 3, PM866:
- receives CNCP (CNCP-master 0)
- no CI855
Controller 4, PM891:
- receives time from SNTP
- sends CNCP-time as CNCP-master 2
- CI855 as MB300 ClockMaster on MB300-net 11
800xA system 1:
- combined AS/CS
- AC800Connect
- AC400Connect
- RTA CLS1-setting 0,2,0
- Reverse_sync_mode = false
- two AC450, both CLS1-setting 0,2,0
800xA system 2:
- two AS + two CS + IM
- AC800Connect
- AC400Connect
- RTA CLS1-setting 0,2,0
- Reverse_sync_mode = false
- three AC450, all with CLS1-setting 0,2,0
The two 800xA systems are independent from each other.
One Control network for all CS/AC800M in both systems.
One ClientServer network for all AS/CS/Clients in both systems.
MB300 nets 11 and 12 is totally separated.
800xA system 1 works. Time diff between PC:s is < 20ms, and AC800M seems to have the correct time.but AC450 does not seem to receive the correct time.
800xA system 1 does NOT work. When I set CI855 on Controller 1 to be MB300 ClockMaster (on MB300-net 12), nothing happened. I could NOT see that AC450 adopted correct time.
When I set CI855 on Controller 2 to be (second) MB300 ClockMaster, all AC450 (on MB300-net 12) got their clocks set to 1985-07-08/19:49:XX!!!
Is it wrong to have two CI855 as masters on the same MB300?
Book (System 800xA NetworkConfiguration System Version 5.1 3BSE034463-510 E page 16+0) says "it is recommended to use a CI855 in AT LEAST ONE AC800M so that the time can be distributed from the Control Network to MB300 via CI855"
Why wont the AC450's get synced?
Anyone has a clue?
Thanks
/Martin
Voted best answer
>"MB300 nets 11 and 12 is totally separated"
This is a problem. By Definition Net12 is the Redundant network for Net11. If this is a totally separate network it should be Net21. If the system time will not synch on Network 12 I'd be very suspicious that this is related.
This is a problem. By Definition Net12 is the Redundant network for Net11. If this is a totally separate network it should be Net21. If the system time will not synch on Network 12 I'd be very suspicious that this is related.
Answers
Minor correction,
It should say: 800xA system 1 does NOT work.
It should say: 800xA system 1 does NOT work.
What is the CI855 setting made in Control Builder M?
With ”No sync” you could theoretically push a wrong time if you are able to startup the clock sync task (see next section)...
1. Use a valid sync direction setting (800M -> CI855) in CBM project
2. SLTARG to CI855 from CS node after DFTARG -1,-1 followed by TSESS, then CTRL-B
3. Check CI855 time with RDATIME. Abort if wrong and go back to step 1.
4. Check CLS1 (FINS 218,1 followed by GINS)
5. Check sync state with: LOCPSET CMDS:TP02.CT followed by LCLKP
6. If necessary, wake up master with RET CXAE000,10
7. Repeat step 5.
8. Check all other nodes with respect to steps 4 and 5. LOCPSET does not need to be repeated.
Two CI855 can have 1,2,1 setting per network. One will act master, the other backup. Do not issue step 6 in more than one node per network. KIT/ACT can be used to bring down an undesired master.
Be very observant on system messages, revert with full detail if you should see clock related messages.
With ”No sync” you could theoretically push a wrong time if you are able to startup the clock sync task (see next section)...
1. Use a valid sync direction setting (800M -> CI855) in CBM project
2. SLTARG to CI855 from CS node after DFTARG -1,-1 followed by TSESS, then CTRL-B
3. Check CI855 time with RDATIME. Abort if wrong and go back to step 1.
4. Check CLS1 (FINS 218,1 followed by GINS)
5. Check sync state with: LOCPSET CMDS:TP02.CT followed by LCLKP
6. If necessary, wake up master with RET CXAE000,10
7. Repeat step 5.
8. Check all other nodes with respect to steps 4 and 5. LOCPSET does not need to be repeated.
Two CI855 can have 1,2,1 setting per network. One will act master, the other backup. Do not issue step 6 in more than one node per network. KIT/ACT can be used to bring down an undesired master.
Be very observant on system messages, revert with full detail if you should see clock related messages.