in Control builder Unwanted Logic connection error and ODB inconsistency error in 800xA 6.0.3..2 system
1.In control builder when doing online Editor in block showing ODB inconsistency Error. (Attached Screenshot for your Ref)
2. During offline mode when going for logic check option from Main menu check unwanted unconnected logics and Errors is coming.(Attached Screenshot for your ref).
For your information this is a HMI conversation project from 5.0 SP1 to 6.0.3.2 system.
Answers
Logic looks corrupted. Question is whether control logic is corrupted in Aspect servers or it is just problem of Engineering PC you are using.
Important is don't make any modifications in logic and don't save.
Try to open the same logic from other station where Control Builder is installed, e.g. from Connectivity server.
I experienced situation that one Engineering station has been showing corrupted code with ODB inconsistency errors, but in Connectivity server CBM the code was shown OK without errors.
That time we could not find other solution than reinstallation of broken Engineering PC from scratch.
Important is don't make any modifications in logic and don't save.
Try to open the same logic from other station where Control Builder is installed, e.g. from Connectivity server.
I experienced situation that one Engineering station has been showing corrupted code with ODB inconsistency errors, but in Connectivity server CBM the code was shown OK without errors.
That time we could not find other solution than reinstallation of broken Engineering PC from scratch.