ACS 880-31 Limits on
Hello,
We are required to use the control panel of the drive in Remote mode as a speed reference using speed reference selection, but when doing so the maximum speed limit is not applied, although it is applied on the control panel speed reference in Local mode.
Thanks,
Mohannad
We are required to use the control panel of the drive in Remote mode as a speed reference using speed reference selection, but when doing so the maximum speed limit is not applied, although it is applied on the control panel speed reference in Local mode.
Thanks,
Mohannad
Answers
Hi
not so clear to understand: your drive is in Remote mode (I think for start/stop function) but you set by Control Panel the reference.
In this case, probably you use parameter 22.11 set to Control panel (ref. saved) and with limits set in parameter group 30 - limits.
I not have understand where you have the issue, could you better explain?
BR
Flavio
not so clear to understand: your drive is in Remote mode (I think for start/stop function) but you set by Control Panel the reference.
In this case, probably you use parameter 22.11 set to Control panel (ref. saved) and with limits set in parameter group 30 - limits.
I not have understand where you have the issue, could you better explain?
BR
Flavio